Originally Posted by infamouspdp
i haven't changed it yet.i just wanted to know how much pressure i should have and the best way to do it.
|
The mineral oil used with R12 is not compatible with the PAG and PAO oils used for R134a. A thorough cleaning and flushing of the system must be done. If you want your R134a charge to last you need to buy 134a compatible hose repalcements or have a set made. All o-rings need to be changed and your comressor needs to be be completely drained of oil and then flushed clean, or replaced with a newer unit with the proper internal o-rings and seals. If yor system uses an orifice tube, a new one for R134a should be installed for best performance. After all that and your ready for charging, vacuum the system down to less than 500 microns for thrity minutes and then check for leaks. If no leaks, continue on for another 30-60 minutes or more. For proper charge, it is best to figure out the weight of refrigerant required. Judging by pressures alone will get you in the ball park, but will not get you right. Low side is most, if not always, the larger pipe and is usually insulated. Ideal pressures should be between 35-45 and 220-250 psi at 77-80*F. Most service manuals will have a temperature/pressure chart for R134a.
Lots of details left out, but that's the canned version.